CA
I want to find a relay that ideally is normally closed (but could live with normally open) that would switch a 350 VAC 650 HZ at about 1A.

This is to control an electoluminesent light off on demand.

Am rather stumped.

Help would be appreciated.

Regards:

Gins
 
Replies continue below

Recommended for you

Most machine tool relays can handle up to 600V and 10A resistive loads - a highly inductive load would require some de-rating.

If you want something beefier, you can go to some type of lighting contactor.
 
Any chance you can switch the line side of the lamp power supply instead? If not, you may be stuck with a vacuum relay such as is used in the RF world, like Jennings Technology. Serious overkill, but you have a tough spec.

"Venditori de oleum-vipera non vigere excordis populi"

 
jraef is right - I totally missed the 650 Hz.

You might look into some type of mechanically-held contactor, but I doubt the coils will function well at that frequency.

There might be some 400 Hz military type relays that could do the job.

 