Hello Fellow Members,
Excuse me for my lack of knowledge, I am a project engineer and putting this topic for clearing my doubts and getting some more electrical knowledge.
Suppose I have 2 switchboards, each switchboard has 2 busbars (so in total 4 busbars). Each busbar will be powered by one generator. Under normal conditions, the switchboards and busbars will form a closed ring operation. The switchboard busbars are interlinked with breakers to form closed ring operation. This mode of operation will give flexibility in terms of generator usage, load sharing and so on.
However, if due to some reason there is a bus fault and the related protection system of bus tie breakers on either side of busbar detects the fault and will isolate the bus to protect other busbars/generator/switchboard section.
Now, my question is.
1. What if fault happens and since circuit breaker is a mechanically operating device, it surely takes a few milliseconds to open. During this milliseconds required for breaker operation, is there a possibility that fault current travels to other busbars before circuit breaker trips?
2. How can other busbar/switchboard busbar protection system with breakers identify that fault is not on our busbar, so healthy busbar breakers do not trip?
Thanks and hoping for your answer.
regards
Excuse me for my lack of knowledge, I am a project engineer and putting this topic for clearing my doubts and getting some more electrical knowledge.
Suppose I have 2 switchboards, each switchboard has 2 busbars (so in total 4 busbars). Each busbar will be powered by one generator. Under normal conditions, the switchboards and busbars will form a closed ring operation. The switchboard busbars are interlinked with breakers to form closed ring operation. This mode of operation will give flexibility in terms of generator usage, load sharing and so on.
However, if due to some reason there is a bus fault and the related protection system of bus tie breakers on either side of busbar detects the fault and will isolate the bus to protect other busbars/generator/switchboard section.
Now, my question is.
1. What if fault happens and since circuit breaker is a mechanically operating device, it surely takes a few milliseconds to open. During this milliseconds required for breaker operation, is there a possibility that fault current travels to other busbars before circuit breaker trips?
2. How can other busbar/switchboard busbar protection system with breakers identify that fault is not on our busbar, so healthy busbar breakers do not trip?
Thanks and hoping for your answer.