I have two quick questions (or sanity checks).
1. Am I correct in thinking that pipework, silencers etc on the discharge side of a relief valve should be sized using the un-derated flow of the relief valve and NOT the derated flow?
2. When the relief case is from a single pressure reducing valve I would assume the valve to be in the fully open position. My downstream pressure would be the relief valve set point + 10% overpressure. Is the upstream pressure taken as the MAWP of the upstream system (or the upstream relief protection set-point if lower than MAWP). Does the API 520 or 521 give any detail (i.e. to use the RV setpoint upstream) on this point?
Many thanks in anticipation for your help.
Regards
Benjymac
1. Am I correct in thinking that pipework, silencers etc on the discharge side of a relief valve should be sized using the un-derated flow of the relief valve and NOT the derated flow?
2. When the relief case is from a single pressure reducing valve I would assume the valve to be in the fully open position. My downstream pressure would be the relief valve set point + 10% overpressure. Is the upstream pressure taken as the MAWP of the upstream system (or the upstream relief protection set-point if lower than MAWP). Does the API 520 or 521 give any detail (i.e. to use the RV setpoint upstream) on this point?