denstan
Mechanical
- May 26, 2002
- 8
Anyone out there can help me with this. In ASME B31.1 Appendix II there is a method for Relief Valve Discharge Piping Design. One of the equations is to determine the pressure at the vent exit P3. In certain cases P3 calculated by this equation can be less than atmospheric (14.7 Psia). From other sources I have come across, if this occurs in the pipework sizing then the exit pressure P3 must be set to atmospheric (14.7 Psia) and the process is to work backwards along the pipe to determine if the calculated pressure drop causes a problem. My problem is that ASME B31.1 does not warn the user that if the calculated value of P3 is less than atmospheric then P3 must be set to atmospheric.The example given is such that P3 is well above the atmospheric pressure hence no problem.
If I consider the other sources then by setting P3 to atmospheric, then calculate P2,V2 and check for blowback then you get a problem. On the other hand if you use the calculated value of P3 and calculate P2,V2 then blowback is not a problem. Please advise.
Regards
DSB