I am pretty sure we discussed this before....but I was trying to run thru my notes and did a search but didnt find what I was looking for.
Given a 208wye system, leg to leg connections to a load (single phase load). Each load draws 14A. So, if I have 3 loads, balanced across the legs (AB,AC,BC) each LEG will have a total current draw that is additive so 28A would be the draw on each leg. Correct?