I have a solution to a problem here, that I would like to have checked by someone in the know, if anyone can spare the time.
I was wondering about a simple problem...Let's say I have a room of a given size. Also assume that the walls of the room are perfect insulators. The heat energy that is in the room cannot leak out through the walls, and no heat from outside the room can leak in. It is more a huge box than a room with windows and doors, except that a "perfect" air conditioner is included too. All heat transfer from the room will occur through the air conditioner system.
Now, let's say that the temperature in the room is 90degF, and I want to drop the temperature down to 77degF. I know that there is latent heat in the system, but I don't care about that because I just want to remove 13degF of "visible" heat from the room, which is immediately sensed as temperature. Therefore, I assume the following equations should give me the equivalent amount of energy for one molecule in the room:
T_hot = 90 degF (32.222 degC) = 305.372 degK
T_cold = 77 degF (25 degC) = 298.15 degK
deltaT = T_hot - T_cold = 7.222 degK
deltaT = E_m / k, where:
deltaT = differential temperature (degK)
E_m = energy (joules) of the molecule
k = the Boltzmann Constant (1.38x10^-23 joule/degK).
Therefore, E_m = k*T
Doing the math:
E_m = 1.38x10^-23 joule/degK * 280.372 degK = 3.87x10^-21 joule, of kinetic energy in one molecule in the room.
Now, according to the Ideal Gas Equation, which should be fine for conditions relatively close to STP:
P*V = n*R*T, where:
P = Gas pressure (pascals) = 1atm = 101325 pascal
V = Volume of the room (m^3) = 5m * 6m * 5m = 150m^3
n = Number of moles of gas in the room (mol)
R = Gas Constant (8.314 joule/(degK*mol))
T = T_hot, temperature of room before cooling has begun (degK) = 305.372 degK
Therefore, n = (P*V) / (R*T)
Doing the math:
n = (101325 pascal * 150m^3) / (8.314 joule/(degK*mol) * 305.372 degK) = 5986.44 mol of particles in the room.
Then, the total amount of energy we want to remove from the room is:
E_tot = E_m * n * Avogadro's Number, where:
Avogadro's Number = 6.022x10^23
Doing the math:
E_tot = 3.87x10^-21 joule * 5986.44 mol * 6.022x10^23 = 13951482.23 joules
Converting to KW-Hr (where 1 joule = 2.78x10^-7 KW-Hr):
E_tot = 3.86 KW-Hr
Now assuming an air conditioner rated at 48000 BTU/Hr of power, and disregarding any losses:
1 BTU/Hr = .00029 KW, so 48000 BTU/Hr = 13.92 KW
Finally,
TimeToCool = E_tot / 13.92 KW = .28 Hr = 16.8 min
Does this sound right to anyone? I know the numbers are in the correct range, but is that a coincidence, or is my math sound?
Thanks for any responses!
I have a solution to a problem here, that I would like to have checked by someone in the know, if anyone can spare the time.
I was wondering about a simple problem...Let's say I have a room of a given size. Also assume that the walls of the room are perfect insulators. The heat energy that is in the room cannot leak out through the walls, and no heat from outside the room can leak in. It is more a huge box than a room with windows and doors, except that a "perfect" air conditioner is included too. All heat transfer from the room will occur through the air conditioner system.
Now, let's say that the temperature in the room is 90degF, and I want to drop the temperature down to 77degF. I know that there is latent heat in the system, but I don't care about that because I just want to remove 13degF of "visible" heat from the room, which is immediately sensed as temperature. Therefore, I assume the following equations should give me the equivalent amount of energy for one molecule in the room:
T_hot = 90 degF (32.222 degC) = 305.372 degK
T_cold = 77 degF (25 degC) = 298.15 degK
deltaT = T_hot - T_cold = 7.222 degK
deltaT = E_m / k, where:
deltaT = differential temperature (degK)
E_m = energy (joules) of the molecule
k = the Boltzmann Constant (1.38x10^-23 joule/degK).
Therefore, E_m = k*T
Doing the math:
E_m = 1.38x10^-23 joule/degK * 280.372 degK = 3.87x10^-21 joule, of kinetic energy in one molecule in the room.
Now, according to the Ideal Gas Equation, which should be fine for conditions relatively close to STP:
P*V = n*R*T, where:
P = Gas pressure (pascals) = 1atm = 101325 pascal
V = Volume of the room (m^3) = 5m * 6m * 5m = 150m^3
n = Number of moles of gas in the room (mol)
R = Gas Constant (8.314 joule/(degK*mol))
T = T_hot, temperature of room before cooling has begun (degK) = 305.372 degK
Therefore, n = (P*V) / (R*T)
Doing the math:
n = (101325 pascal * 150m^3) / (8.314 joule/(degK*mol) * 305.372 degK) = 5986.44 mol of particles in the room.
Then, the total amount of energy we want to remove from the room is:
E_tot = E_m * n * Avogadro's Number, where:
Avogadro's Number = 6.022x10^23
Doing the math:
E_tot = 3.87x10^-21 joule * 5986.44 mol * 6.022x10^23 = 13951482.23 joules
Converting to KW-Hr (where 1 joule = 2.78x10^-7 KW-Hr):
E_tot = 3.86 KW-Hr
Now assuming an air conditioner rated at 48000 BTU/Hr of power, and disregarding any losses:
1 BTU/Hr = .00029 KW, so 48000 BTU/Hr = 13.92 KW
Finally,
TimeToCool = E_tot / 13.92 KW = .28 Hr = 16.8 min
Does this sound right to anyone? I know the numbers are in the correct range, but is that a coincidence, or is my math sound?
Thanks for any responses!