GregLocock
Automotive
- Apr 10, 2001
- 23,641
Bit of a tricky set of charts to understand. Basically they look at various amounts of overbuild, and then 0 3 or 12h of storage. https://pmc.ncbi.nlm.nih.gov/articles/PMC8536784/pdf/41467_2021_Article_26355.pdf
For example, if you have 3h of storage for Australia, and build 100% of nominal demand in renewables, for 1 hour a year 70% of the power will not be there, and for all but 2500 hours the grid will be fully powered up. This is rather interesting. Increasing the storage doesn't help much. If we beef up the overbuild to 150% then the 1h outage figure is 50% (ish) and for all but 150 hours the grid will be fully powered. If you then fit 4 times as many battery, ie 12h, the numbers fall to 10% and 15 hours. If you double up on generation again, ie 300% nominal, you get the same performance with no storage at all. So you can see that if 12h of storage costs less than 150% of generation you should do that (possibly). Bear in mind these aren't plate capacity, a 4 MW wind turbine generates about 1.3 MW of power on average, a 1 MW solar panel is about 0.17 MW on average. For Australia in a different chart they think that for 150%/3h storage you should be about 70% wind, 30% solar, and we want 24 GW, so that's a fleet of 24*.7*1.5*3 =75 GW of turbines, 24*.3*1.5*6 GW of solar panels, 65 GW, and of course 3*24=72 GWh of batteries. That's about half a trillion dollars . If you just use gas it would be more like 50 Billion dollars plus the cost of the gas
I think this is a good start at looking at the tradeoffs.