5747hazel
- Dec 28, 2019
- 43
I copied section 405.2.3.1 for evaluation from IEBC as below
"405.2.3.1 Evaluation. The building shall be evaluated by a registered design professional, and the evaluation
findings shall be submitted to the code official. The evaluation shall establish whether the damaged building, if
repaired to its pre-damage state, would comply with the provisions of the International Building Code for for load
combinations that include wind or earthquake effects, except that the seismic forces shall be the reduced seismic
forces."
my question is what edition of strength codes to use. say it is a steel building, which edition of AISC to use. same question applies to ACI. also for repair
"405.2.3.3 Extent of repair for noncompliant buildings. If the evaluation does not establish that the building
in its predamage condition complies with the provisions of Section 405.2.3.1, then the building shall be retrofitted
to comply with the provisions of this section . The wind loads for the repair and retrofit shall be those required by
the building code in effect at the time of original construction, unless the damage was caused by wind, in which
case the wind loads shall be in accordance with the International Building Code. [partial shown]"
which edition of steel and concrete codes to use for code checking? further more wind loads from ASCE 7-05 or earlier edition might not compatible with current ACI or AISC and other codes for material strength.
I am assuming they all should be current edition. any comments? thanks
forces."