electricpete
Electrical
- May 4, 2001
- 16,774
We are doing an electrical test which will require repeated starts of a motor. The total number of starts will be 10 or 20 or more We would like to accomplish the repeated starts in the minimum time which will not jeopardize the health of the motor (this is a critical motor and we have no spare readily available). I am trying to provide input on the duty cycle.
The motor is 60 hp, 2-pole, low-inertia load = centifugal pump.
NEMA MG-10-2001 Table 7 linked in faq237-1285 gives the following limits:
Maximum 3.2 starts per hours
Minimum 170 sec "off-time" between starts.
Although not tabulated, it is noteworthy that the motor cools faster while running between starts than while resting (since much more heat is generated during start than run, and much more cooling due to airflow occurs while running than while secured). Ideally, considering the critical nature of the motor and lack of spare, I would be comfortable with the following simple duty cycle which maximizes the run-time between starts:
* Start and run for minimum 15 minutes
* Stop and rest for minimum 5 minutes
* Repeat
However there is a problem with the above. This cycle is difficult for the fluid system to accommodate. I believe that if the system is not started up for continuous run, then the pump must be shut down in 5 minutes due to fluid system considerations. For the sake of this discussion, assume we do not want to uncoupled the motor from the pump. The cycle that appears to be needed to for consistency with plant needs is as follow:
* Start and run for 5 minutes
* Stop and rest for T minutes
* Repeat
What would you recommend for T (above) ? I think that a literal interpretation of the standard would allow T = 15 minutes, but my gut tells me we need to go much longer.
=====================================
Eng-tips forums: The best place on the web for engineering discussions.
The motor is 60 hp, 2-pole, low-inertia load = centifugal pump.
NEMA MG-10-2001 Table 7 linked in faq237-1285 gives the following limits:
Maximum 3.2 starts per hours
Minimum 170 sec "off-time" between starts.
Although not tabulated, it is noteworthy that the motor cools faster while running between starts than while resting (since much more heat is generated during start than run, and much more cooling due to airflow occurs while running than while secured). Ideally, considering the critical nature of the motor and lack of spare, I would be comfortable with the following simple duty cycle which maximizes the run-time between starts:
* Start and run for minimum 15 minutes
* Stop and rest for minimum 5 minutes
* Repeat
However there is a problem with the above. This cycle is difficult for the fluid system to accommodate. I believe that if the system is not started up for continuous run, then the pump must be shut down in 5 minutes due to fluid system considerations. For the sake of this discussion, assume we do not want to uncoupled the motor from the pump. The cycle that appears to be needed to for consistency with plant needs is as follow:
* Start and run for 5 minutes
* Stop and rest for T minutes
* Repeat
What would you recommend for T (above) ? I think that a literal interpretation of the standard would allow T = 15 minutes, but my gut tells me we need to go much longer.
=====================================