We are experiencing repetitive firetube leaks on two steam boilers serving a laundry.
(York-Shipley 100HP, 150 PSI design, burning Diesel Oil)
This has been dragging for some time, and we are sure that we have no issues in Water Treatment, no short-cycling, no batch loading, no thermal shocks.
The boiler are turned on in the morning, and are operated until early afternoon, then turned off. To make sure that we are not feeding the boiler with cold water at the morning startup, we have added an electric heater in the feedwater tank, to keep it at 60C.
All the leaks ever experienced were tube attachment leaks (tube attachment weeping), never tube ends cracks. There is no correlation in the location of the tube failures.
- Boilers were started up Nov.2014
- Feb. 2017 : Reroll boiler A (few tubes)
- Mar. 2017 : Reroll boiler B (few tubes)
- Apr. 2017 : Reroll Boilers A and B (few tubes)
- May. 2017: Reroll Boiler A (few tubes)
- Feb. 2018 : Reroll Boiler A (All 2nd pass of tubes)
- Dec. 2018: Electric Heater installation in feed unit.
- Dec. 2019: Reroll Boiler B (All 2nd pass of tubes)
- Dec. 2020: Replacement 2nd pass of tube Boiler A
- May 2021: Replacement 2nd pass of tube Boiler B
- Dec. 2021: Reroll Boiler B (10 tubes)
- Apr. 2022: Reroll boiler A (5 tubes).
We are really out of arguments as to why this could happen. Would anyone around think of any possible cause?
(York-Shipley 100HP, 150 PSI design, burning Diesel Oil)
This has been dragging for some time, and we are sure that we have no issues in Water Treatment, no short-cycling, no batch loading, no thermal shocks.
The boiler are turned on in the morning, and are operated until early afternoon, then turned off. To make sure that we are not feeding the boiler with cold water at the morning startup, we have added an electric heater in the feedwater tank, to keep it at 60C.
All the leaks ever experienced were tube attachment leaks (tube attachment weeping), never tube ends cracks. There is no correlation in the location of the tube failures.
- Boilers were started up Nov.2014
- Feb. 2017 : Reroll boiler A (few tubes)
- Mar. 2017 : Reroll boiler B (few tubes)
- Apr. 2017 : Reroll Boilers A and B (few tubes)
- May. 2017: Reroll Boiler A (few tubes)
- Feb. 2018 : Reroll Boiler A (All 2nd pass of tubes)
- Dec. 2018: Electric Heater installation in feed unit.
- Dec. 2019: Reroll Boiler B (All 2nd pass of tubes)
- Dec. 2020: Replacement 2nd pass of tube Boiler A
- May 2021: Replacement 2nd pass of tube Boiler B
- Dec. 2021: Reroll Boiler B (10 tubes)
- Apr. 2022: Reroll boiler A (5 tubes).
We are really out of arguments as to why this could happen. Would anyone around think of any possible cause?