Dear guys we have a dc motor with a capacity of 1000 kw with following specs.
- Rated Voltage : 700 vdc
- Rated current : 1700 Amperes
- Type : Seperately excited
-Drive System : Motor generated set( sure its an old system but nevertheless useful) with 4th quadrant control, the motor is being used for reverseable plate rolling mill.
The motor is fitted with a single pole High speed circuit breaker of below specs.
- rated voltage : 1000 vdc
- Current range 3000-4000 amperes presettable and our setting is 3800 amperes.
So far everything is fine but we want to have an spare breaker set for the above rating but the cost of the same seems reasonably high.Now my question is if we can use a VCB of 2000 amperes,12000 ac volts/50 hz (As I have one spare in my store) by connecting in parallel arrangements to match the current requirement while using the same existing sensing and tripping devices.I am aware of the fact about the natural tendency of alternating current's arc quenching capabilty but as the dc voltage is only the 1/17th of VCB,s rated voltage so curious about its possibility.Kindly let me know the possibilty of this option.
regards
- Rated Voltage : 700 vdc
- Rated current : 1700 Amperes
- Type : Seperately excited
-Drive System : Motor generated set( sure its an old system but nevertheless useful) with 4th quadrant control, the motor is being used for reverseable plate rolling mill.
The motor is fitted with a single pole High speed circuit breaker of below specs.
- rated voltage : 1000 vdc
- Current range 3000-4000 amperes presettable and our setting is 3800 amperes.
So far everything is fine but we want to have an spare breaker set for the above rating but the cost of the same seems reasonably high.Now my question is if we can use a VCB of 2000 amperes,12000 ac volts/50 hz (As I have one spare in my store) by connecting in parallel arrangements to match the current requirement while using the same existing sensing and tripping devices.I am aware of the fact about the natural tendency of alternating current's arc quenching capabilty but as the dc voltage is only the 1/17th of VCB,s rated voltage so curious about its possibility.Kindly let me know the possibilty of this option.