edison123
Electrical
- Oct 23, 2002
- 4,462
We have a client with a large chunk of outgoing aluminum cylindrical (280 mm OD/260 mm ID = about 8500 sq mm cross section) busbars of a 11 KV, 50 MW, hydrogen cooled generator failing disastrously for about a length of 4 meters. All three phases and neutral busbars have failed and it was all a molten aluminum disaster in the pit.
I am planning to change these sections into copper bus bars of size about 200x20 mm rectangle. The generator current is about 3300 Amps.
Any one see any problems with this?
Also, I am wondering why aluminum outgoing busbars have been a standard for TG sets?
Muthu
I am planning to change these sections into copper bus bars of size about 200x20 mm rectangle. The generator current is about 3300 Amps.
Any one see any problems with this?
Also, I am wondering why aluminum outgoing busbars have been a standard for TG sets?
Muthu