There is an existing overhead utility line that feeds a 12.47kV-480V, Delta-Wye 2500 kVA transformer that has E-rated fuses at the primary of the transformer. For reliability they are changing this feeder out and running underground cable directly from the Utility's switchgear to a new 12.47kV outdoor metal clad switchgear. The new switchgear has been specified with a vacuum breaker and relay with (3)CTs, one to go around each of the phase conductors. This will replace the E-rated fuses.
I would have thought the CTs would be connected in a residual way so to give the 51N function. Is this common to do it this way ?
I would have thought the CTs would be connected in a residual way so to give the 51N function. Is this common to do it this way ?