redlinej
Electrical
- Mar 13, 2012
- 105
hello everyone,
The problem I am having is that I replaced a Stanford MX341 AVR with a MX321 AVR. The 341 is a good working avr, but the genset is going to be synchronize with two other gensets with 321.This is why we replace the 341 with the 321.The problem I am having with the new avr is that the voltage is not coming up to nominal voltage, its around 365 v (480 nominal).
This is what I think is wrong but cannot see how it can affect the regulation, so hope you guys can help.
The 341 is a two phase sensing avr and the 321 is a 3 phase sensing avr, and the manual say to use a open delta isolation transformer and I did not, instead I place the sensing at the mid point of the series wye connection.the nominal voltage for the genset is 480 V 60 hz and the avr is power from a PMG(120 hz).
The problem I am having is that I replaced a Stanford MX341 AVR with a MX321 AVR. The 341 is a good working avr, but the genset is going to be synchronize with two other gensets with 321.This is why we replace the 341 with the 321.The problem I am having with the new avr is that the voltage is not coming up to nominal voltage, its around 365 v (480 nominal).
This is what I think is wrong but cannot see how it can affect the regulation, so hope you guys can help.
The 341 is a two phase sensing avr and the 321 is a 3 phase sensing avr, and the manual say to use a open delta isolation transformer and I did not, instead I place the sensing at the mid point of the series wye connection.the nominal voltage for the genset is 480 V 60 hz and the avr is power from a PMG(120 hz).