Well, at startup, I didn't suppose that building a transformer could be a thrilling activity.
ScottyUK: -Yes, indeed, there are environmentall problems with SF6, but if I remember correctly, not with the ozone but with warming potential. However, it is bad anyway. And this is the reason for bringing in discution R134a.
-In a normal transformer it shouldn't be an electric arc present, except in the switchgear, but this one is a laboratory transformer and it hasn't switches in it. So it shouldn't be a problem with decomposition products by means of an arc. I think.
Cuky2000: -The tables submited by you are for freons indeed, but R134a is not there. Or R113 is the same with R134a? I think that the breakdown voltage is somwere there like for R12, but I didn't found any datasheet.
- The dissociation products are highly corrosive for both gases, but SF6 is self healing (I don't know the recovery time, anyway). So if there is no electric arc to decompose SF6, would be the replacement with R134a a problem?
I mention again that atmosferic overvoltage (lightning) shouldn't be a problem (only if the user will keep the window open

), but I'll specify this in MSDS).
- Maintain voltages below corona forming. Well, may God help me to get rid of Corona. An ideea about how to track if there it is a Corona development potential is to keep the transformer at atmosferic pressure and to apply at the primary winding a voltage at such level that the secondary E-fields to be the same like in presurized tank, and to look about Corona. At midnight time...spooky thing!
CarlPugh: - The transformer is 220V/100kV, because it has a primary limiting resistor, in such way that at maximum current the maximum voltage will be 50kV.
This transformer will operate in a test station for dielectric materials, so there will be MANY shortcircuits. I built some HV test stations before but only up to 15kV and the transformers were bought. However, I solved the current limiting problem in the same way.
Of course there are other means too for limiting the currents and the voltages, wich are included in the automation station for this project. Two PLC's and a computer are making the "smart things".
One question: why do you say " If there are arcs in a vacuum, you will have problems."? In the vacuum can't be a pressure rising. Or maybe I didn't understood your statement?
- A pressure sensor and a manometer it are mounted on transformer so it will not work in the case of a leakage. If my container is filled with SF6/R134a above atmospheric pressure, I think that is difficult to have air entering in sistem. But indeed, if the presurre get down to 1 bar, it may be safe to vacuum again the transformer and only then refill it.
- About vacuum. If I make vacuum before filling, the water must get out with air I think. The insulator between windings is Nomex. I think it should not absorb water. Is this so?
The vacuum pump can make 10Pa (150microns Hg column?). Would be enough this vacuum? And how long I must mainatain it?
I have not the facilities for passing dried N2 before filling so I must see if another mean to get out the water vapors is possible. Wouldn't it go along with air?
Men, am I in trouble?
Thank you again!