stookeyfpe
Specifier/Regulator
- Mar 13, 2005
- 1,882
This question is based on the 2007 edition of NFPA 14 but feel free to use the current edition because the requirement hasn't changed.
I have a 32 story high-rise I'm currently reviewing for compliance. The maximum churn pressure for the fire pump is 287 PSIG. The standpipe is constructed using Allied Tube & Conduit Schedule 10 pipe which is listed for pressures to 300 PSIG. It will be assembled using Victaulic Style 005 Firelock grooved couplings which for 6-inch pipe is listed for pressures to 300 PSIG.
NFPA 14 Section 11.4.1 states:
As the AHJ I can require a hydrostatic pressure test of 350 PSIG to the standpipe and fittings based on the referenced section. I would like confirmation if you agree or disagree with my interpretation. I know it's a simple question but I haven't done a high-rise in over a year but in the next 6 months I'll be doing at least 5 standpipe/sprinkler plan reviews on high-rise buildings so I'm asking for guidance.
Thank you.
I have a 32 story high-rise I'm currently reviewing for compliance. The maximum churn pressure for the fire pump is 287 PSIG. The standpipe is constructed using Allied Tube & Conduit Schedule 10 pipe which is listed for pressures to 300 PSIG. It will be assembled using Victaulic Style 005 Firelock grooved couplings which for 6-inch pipe is listed for pressures to 300 PSIG.
NFPA 14 Section 11.4.1 states:
All new systems, including yard piping and fire department connections, shall be tested hydrostatically at not less than 200 psi (13.8 bar) of pressure for 2 hours, or at 50 psi (3.5 bar) in excess of the maximum pressure where the maximum pressure is in excess of 150 psi (10.3 bar).
As the AHJ I can require a hydrostatic pressure test of 350 PSIG to the standpipe and fittings based on the referenced section. I would like confirmation if you agree or disagree with my interpretation. I know it's a simple question but I haven't done a high-rise in over a year but in the next 6 months I'll be doing at least 5 standpipe/sprinkler plan reviews on high-rise buildings so I'm asking for guidance.
Thank you.