- Sep 16, 2004
- 3
I'm evaluating a weight loaded pressure relief valves located at the outlet of a blower.
The protected blower is designed to have a capacity of 2,095 ICFM with inlet condition 70°F and 14.7 psia, discharge pressure of 3 psig and motor speed @ 2,637 RPM.
My PRV is set @ 4 psig. My PRV is fully open @ 25% overpressure, with that says, it will give me a relief pressure of 5 psig (1.25 x 4 = 5).
With these condition, DP = 5 psig and motor speed remains contant @ 2,637 RPM, the blower pressure performance curve shows that the inlet air flow will be increased.
My question is should the outlet of the blower be blocked, what would be the relief capacity? Should it be the design capacity of 2,095 ICFM or the increased capacity @ 25% overpressure?
i thought it would be the increased capacity of 2,180 ICFM however if the suction conditions and motor speed remains constant, the blower shouldnt be pulling in more air. Please help.
Thanks in advance,
Duane Loh
The protected blower is designed to have a capacity of 2,095 ICFM with inlet condition 70°F and 14.7 psia, discharge pressure of 3 psig and motor speed @ 2,637 RPM.
My PRV is set @ 4 psig. My PRV is fully open @ 25% overpressure, with that says, it will give me a relief pressure of 5 psig (1.25 x 4 = 5).
With these condition, DP = 5 psig and motor speed remains contant @ 2,637 RPM, the blower pressure performance curve shows that the inlet air flow will be increased.
My question is should the outlet of the blower be blocked, what would be the relief capacity? Should it be the design capacity of 2,095 ICFM or the increased capacity @ 25% overpressure?
i thought it would be the increased capacity of 2,180 ICFM however if the suction conditions and motor speed remains constant, the blower shouldnt be pulling in more air. Please help.
Thanks in advance,
Duane Loh