mjr6550
Structural
- Jun 27, 2006
- 69
I am a structural engineer and am trying to help out someone with church alterations. They are dividing one restroom into two. The building code official says they need a heat source in each restroom. The one has a heating source and is on a exterior wall. I am told that the other has not exterior exposure on all six sides. Is a heating source typically required per the IMC. Here is what I believe is the relavent code: "1204.1 Equipment and systems. Interior spaces intended for
human occupancy shall be provided with active or passive
space-heating systems capable of maintaining a minimum
indoor temperature of 68°F (20°C) at a point 3 feet (914 mm)
above the floor on the design heating day.
Exception: Interior spaces where the primary purpose is
not associated with human comfort."
Can I assume that passive heating is the heat transfer from the surrounding areas?