Resetting Time for Integrator

Status
Not open for further replies.

whatiscontrols

Mechanical
Dec 19, 2006
5
I'm trying to model a PI controller.

The way it works is that for every 5 minutes of positive error an integrator number is incremented by 1. I want to know how to "reset" the timer for the discrete-time integrator so that when there is a zero crossing (i.e. positive to negative) a timer will start at 0 (and if it stays at negative for 5 minute) decrease integrator number by 1...

Please help if you can, I am new to Simulink.
 
Replies continue below

Recommended for you

What you are trying to do isn't right in so many ways.
The PI equation should be put in an interrupt that occurs every T seconds or minutes. The operating system should take care of ensuring the interrupt occurs at intervals of T.

Never use a timer to activate an even every T. You will accumulate error between the time the timer expires and the time it is reset. Use interrupts or a free running clock if you must.

Here is how you implement a simple PI.

E(n)=SP(n)-PV(n)
CO(n)=CO(n-1)+Kc*((T/Ti)*e(n)+(e(n)-e(n-1)))

Where:
n is the period index
E is the error at period n
SP is the set point
PV is the process variable ( feeback )
CO is the control output
Kc is the controller gain
T is time between sample n and n-1.
Ti is the integrator time constant.

One can simplify the equation above
K0 = Kc*(1+T/Ti)
K1 = -Kc
CO(n)=CO(n-1)+K0*e(n)+K1*e(n-1)

Now the PI controller is just a couple of multiplies and adds. Simple. It is best to use floating point or at least 32 bit math. The trick is finding the right values Kc and Ti.




 