Okay, I readily admit my understanding and use of the ACI 318 is still quite limited. I'm much more comfortable with the NDS and everything having to do with wood engineering.
I've recently been doing some work on some detached garages. One story structures with a 24" stemwall resting on a separately poured concrete footer. As far as sizing the footer width, I've usually just looked at the total load at the highest loaded section of wall and if does not exceed 1500 psf (default allowable soil bearing pressure) then I'm good to go.
However, the designer on two very similar projects called out a 6" stemwall on one and a 8" stemwall on the other. Is there a quick, rational check/calculation that I can do to verify that the stemwall size is adequate without getting to muddled up with the details.
My first thought was to simply take the load on the stemwall at is base (so that it includes the selfweight of the stemwall) and check the pressure and compare that to the strength of the concrete (2500 - 3000 psi). However, with the reinforcing (horizontal and vertical) this is probably to simplistic of an approach. I guess it time to really crack open the ACI 318.
I've recently been doing some work on some detached garages. One story structures with a 24" stemwall resting on a separately poured concrete footer. As far as sizing the footer width, I've usually just looked at the total load at the highest loaded section of wall and if does not exceed 1500 psf (default allowable soil bearing pressure) then I'm good to go.
However, the designer on two very similar projects called out a 6" stemwall on one and a 8" stemwall on the other. Is there a quick, rational check/calculation that I can do to verify that the stemwall size is adequate without getting to muddled up with the details.
My first thought was to simply take the load on the stemwall at is base (so that it includes the selfweight of the stemwall) and check the pressure and compare that to the strength of the concrete (2500 - 3000 psi). However, with the reinforcing (horizontal and vertical) this is probably to simplistic of an approach. I guess it time to really crack open the ACI 318.