Residential Floating Stairs Design
SarBear
Hi everyone,
I have been asked to engineer a set of floating stairs for a residential project. I have attached the PDF from the steel fabricator below. The idea is that the treads are HSS 10x2x1/4, and each tread is to weld to a 1" thick x 10" tall "spandrel" plate that forms the exterior perimeter of the stairs. On the sides of the stairwell this plate will be welded to supporting HSS columns every 3' or so. At the rear of the stairwell the plate will be bolted directly into concrete along its length. These are the different aspects of the stairs that I think I need to look at:
1. The capacity of the HSS treads themselves (easy enough, they are each cantilever beams)
2. The capacity of the weld from the HSS treads to the spandrel plate (easy enough)
3. The capacity of the spandrel plate as it spans between supporting columns and bolts (no idea how to take into account the torsions that are introduced into the plate from each tread)
4. The capacity of the weld from the spandrel plate to the columns (need to get the reactions at each column from #3)
5. The capacity of the columns (can't do this until #3 is done)
6. The connection from the spandrel plate to the supporting I-beam at the top of the stairs (can't do this until #3 is done)
7. The connection from the HSS columns to the concrete slab at the bottom
8. The connection from the HSS columns to the framing at the top (is this needed?)
How would you go about designing these stairs? Some items like #1 and #2 are easy to calculate, but I'm totally lost on how #3 is to be done since each tread is imparting a shear and a torsion to the spandrel plate. I've looked around for hours for some kind of example or design guide but I can't find anything useful. I'd describe the spandrel beam calculation as a "beam fixed at both ends with point loads and torsional loads" if that sounds correct. Do you have any recommendations for examples, software, or guides that I could check out?
 https://files.engineering.com/getfile.aspx?folder=85f840b7-1d99-498f-8a1a-1deca48c1f6f&file=ESCALERA_LOTE_32-Model.pdf
I've done stairs with the setup you're describing. A simplified approach would be to treat the edge of your plate as a strip spanning between the supports, with a point load from the tension/compression couple of the tread. You'd need to sort out an effective width you are comfortable with. I don't see any railing in your sketch but I did a similar stair when I was younger and more paranoid and did a separate model that accounted for the railing providing a little bit of continuity between tread tips, in that case they had a decorative steel railing that turned up off of each tread and had some connectivity.