Residual earth fault protection
kaspor
52
Hello
I am trying to understand whether there's inaccuracies with earth fault currents detected with a residual scheme (i.e. CT's connected in STAR to protection relay, protection relay measures imbalance current to determine earth fault current).
Can you please confirm if my understanding is correct for these 3 scenarios:
1. Assume DELTA/STAR transformer supplies an unloaded switchboard. During a supply cable earth fault on A phase, no current will flow through B and C phases. Residual current detected by protection relay is A phase current.
2. Assume DELTA/STAR transformer supplies a STAR connected motor (assume initially operating at 100A). During a supply cable earth fault on A phase, earth fault current (assume 1000A) will flow from phase A to ground. No current will flow through B & C phases (due to STAR connected motor). Residual current detected by protection relay is A phase current.
3. Assume DELTA/STAR transformer supplies a DELTA connected motor (assume initially operating at 100A). During a supply cable earth fault on A phase, earth fault current (assume 1000A) will flow from phase A to ground. Phase B and C current will circulate through the DELTA winding and return back to the transformer. Protection relay will not see 1000A, but instead the vector summation of Ia+Ib+Ic? Does this mean the earth fault current seen by the relay will be inaccurate?
IMO, assuming residual earth fault protection on Star side:
In Scenario-1, any fault in A-phase will return back through neutral / ground, there is no other path available. Conclusion seems OK.
In Scenario-2, Some current will reflect in B&C phases, due to impedance of neutral path and magnetic coupling of widings. Residual current will be Ia+Ib+Ic, like in scenario-3.
The back EMF of the motor will back-feed about four times full load current into a supply conductor fault regardless of the motor internal connection.