Hi David. This is what I believe that he means:
Consider three PTs connected Wye

elta with the wye point grounded. Now remove one of the CTs and leave the other two.
The PTs must have a high impedance compared to the system impedance to ground so as to maintain a reasonable neutral position.
Now, if either of the phases with the PTs is grounded, the other PT secondary voltage will rise to reflect line to line voltage.
If the unmetered phase is faulted to ground then the voltage of both PTs will rise to reflect line to line voltage.
You have to detect the grounded phase condition by looking at the over-voltage on at least one of the unfaulted phases.
As I hinted, probably not ready for prime time.
I can't see you ever considering this solution on your system, David.
Remember the ground detector lights on the old 440 Volt Delta systems?
When a phase went to ground, one light went out and the other two got brighter.
If a one lamp burned out, It looked like a grounded phase BUT the other two lamps did not increase in brightness.
A similar situation here. Look for the voltage
Rise.
Bill
--------------------