Can anyone tell me how the temperature correction factors are derived for correcting resistance to 25C in an electric motor?

thanks, mb
 
Replies continue below

Recommended for you

Assuming it is a copper winding, the resistance temperature coefficient is 1/234.5 per deg C at 0 deg C.


R2 = (R1)*(234.5+T2)/(234.5+T1)

Where R1 is the known (or measured) resistance at temperature T1 deg C

T2 is the temperature in deg C for which you want to know the new resistance R2

*Even inside a hard-boiled egg, there is a golden heart!!!*
 
Thanks edison,

Now the next question. Is there a temperature correction factor that can be applied to the viscosity of varnish in order to standardize the measurements? If so, do you know what it might be? Thnaks, mb
 