tin2779
Electrical
- May 26, 2007
- 38
A contractor submitted a test proposal and added a small note:
"Please see that if GPR as well as the step and touch potentials cannot be achieved as required, additional on-site testing will be required and the possibility of having
a remote ground grid may have to be considered,".
I am just wondering that remoted grid will only help in reducing GPR but not in step and touch potential. Is this correct ?
Thanks
"Please see that if GPR as well as the step and touch potentials cannot be achieved as required, additional on-site testing will be required and the possibility of having
a remote ground grid may have to be considered,".
I am just wondering that remoted grid will only help in reducing GPR but not in step and touch potential. Is this correct ?
Thanks