Hi friends little off topic but important for me.
We have project - hotel resort type in Sri Lanka, 75 rooms separated to 2 storeys buildings per 4 rooms each with area of footprint 140 m2 each allocated within 20 m from each other.
Local fire department issued requirements to make :
Hose reel System 11*19 mm* 30 m hose reel providing 30 l/m with 6 m throw
and
Fire Hydrant System
Pillar type hydrants 02*65 mm capable to maintain minimum of 300 kpa residual pressure at the 10 l/s whyle two hydrants are operating.
We can ask to reduce requirements to only Hose reel system as hydrants with given capacity very expensive and probably fire department let us do it as the other hotels done it before but is it actually safe to have only hose reel systems without hydrants in such kind of objects?