The motor is started across the line and there are no capacitors.
There are actually three of these motors in service and the problem is from time to time these motors blow a 9R fuse in the starter. Usually, but not always, the fuse blows when the motor is started. I talked about this in thread 237-178916. I just replaced the mechanical overloads and relays in each of the starters with a Multilin 469 so I could understand what is going on.
When I started up one of the machines for the first time after installing the 469 I got a single phasing trip with currents of A = 624A, B = 622A,C = 0A. The trip was 5 seconds after starting (the motor takes ~12 secs to get up to speed). The 469 trips on single phasing after two seconds so it looks like the C phase 9R fuse blew after 3 seconds. The other two motors started up with no problems this time.
I measured the resistance of the A and B fuses with a digital low resistance ohmmeter (I am not certain how good this is for determining the health of a fuse, but it was interesting.)The A phase fuse measured 1.8 milliohms, B phase fuse measured 4.4mohms, and a new fuse measured 1.8 mohms. Since the B phase fuse resistance was 2.5 times a new fuse I replaced the B phase fuse along with the blown C phase fuse. After this the motor starting up fine and is running now.
The problem is that 624 amps in 3 seconds should not have blown the 9R fuse. So I now suspect that the fuses are blowing or are severaly damaged because the operators have been restarting the motors too quickly. I have set the Multlin to prevent a restart for 2 minutes.
I appreciate your help and look forward to any other thoughts.