Cerkit
Electrical
- Jan 18, 2016
- 99
Hi,
For a restricted earth fault relay with an effective setting of 0.2A. The CT ratio is 2000:1 and the maximum earth fault current is 800A through an earthing transformer. If there is an earth fault at the end of an LV winding (so covers the entire winding) is it correct that the primary current in the neutral required to operate the relay will be 400A? I calculated this from
0.2A (setting) * 2000 (CT ratio) = 400A
As the full winding is included then I multiply by 1, 400A * 1 = 400A
Thanks
For a restricted earth fault relay with an effective setting of 0.2A. The CT ratio is 2000:1 and the maximum earth fault current is 800A through an earthing transformer. If there is an earth fault at the end of an LV winding (so covers the entire winding) is it correct that the primary current in the neutral required to operate the relay will be 400A? I calculated this from
0.2A (setting) * 2000 (CT ratio) = 400A
As the full winding is included then I multiply by 1, 400A * 1 = 400A
Thanks