Deker
Structural
- Nov 9, 2008
- 368
I've got an architect that would like to build a freestanding site wall using two wythes of breeze block separated by a 2" cavity that will be filled with river rock. The rock will be sandwiched between wire mesh so that it can be seen through the breeze block without falling out of the cavity. See attached sketch.
If I'm basing my design on NCMA TEK 03-16A, I'm limited to a service load of 50 psf on the wall. Assuming these walls are resisting an at-rest retaining pressure of (0.5)(100 pcf)(5') = 250 plf / ft imposed by the rock doesn't even put me in the ballpark of considering this to be feasible, especially considering that I'll need to include the effects of wind and seismic load on the wall.
But the fact that the walls are only retaining a 2" layer of rock has to result in some reduction, right? I understand that fluids exert equal pressure in all directions, but obviously rock is not a fluid and I'm not sure the EFP method is valid in this case. I've seen some threads that cover variations of this issue, namely narrow backfill between a wall and rock face, and I've also looked briefly into applying silo retaining pressure methods, but I'm curious how others would quantify the retaining pressure in this situation.
If I'm basing my design on NCMA TEK 03-16A, I'm limited to a service load of 50 psf on the wall. Assuming these walls are resisting an at-rest retaining pressure of (0.5)(100 pcf)(5') = 250 plf / ft imposed by the rock doesn't even put me in the ballpark of considering this to be feasible, especially considering that I'll need to include the effects of wind and seismic load on the wall.
But the fact that the walls are only retaining a 2" layer of rock has to result in some reduction, right? I understand that fluids exert equal pressure in all directions, but obviously rock is not a fluid and I'm not sure the EFP method is valid in this case. I've seen some threads that cover variations of this issue, namely narrow backfill between a wall and rock face, and I've also looked briefly into applying silo retaining pressure methods, but I'm curious how others would quantify the retaining pressure in this situation.