Chris Poulsen
Civil/Environmental
- Jul 8, 2020
- 1
When designing retaining walls I have referred to the lateral pressures provided by the geotechnical reports. The reports have always included standard active pressure and an active pressure with seismic loading included (e.g. 55 pcf active and 85 pcf active with seismic loading). I have always designed with the seismic loading which is the higher of the two and still designed the walls to with a 1.5 safety factor against sliding and overturning. I just barely noticed a section of the building code (IBC 1807.2.3) which states an exception to the 1.5 safety factor as, "Where earthquake loads are included, the minimum safety factor for retaining walls sliding and overturning shall be 1.1".
From this, it appears that the retaining walls have been over designed at that if the larger active pressure with seismic loading included is used the safety factor can be reduced to 1.1. I have worked with several engineers and none have ever mentioned this before. Am I missing something or is it alright to use a lower safely factor when including seismic loading for the active pressure?
From this, it appears that the retaining walls have been over designed at that if the larger active pressure with seismic loading included is used the safety factor can be reduced to 1.1. I have worked with several engineers and none have ever mentioned this before. Am I missing something or is it alright to use a lower safely factor when including seismic loading for the active pressure?