ktwannabe
Geotechnical
- Apr 11, 2002
- 8
We are working on a site development project where the proposed parking lot will require a 4 foot cut into a short hillside approximately 5 feet away from an existing utility pole. We anticpate installing a retaining wall to support the cut and maintain the stability of the pole. The information we recieved from the utility company indicates the pole is embedded 9.5 feet below grade and has a moment at the ground surface of 286 kip-ft due to wind and ice loading on the pole and wires. The pole is approximately 75 feet high above the ground with 3 wires that are approximately 50 to 60 feet above the ground. The moment seems high to us and we can't get the existing condition to be stable for overturning. The overburden is a dry, residual sandy silt weathered from shale that varies from a friction angle of 34 degrees to 38 degrees based on SPT correlations. The overburden is approximately 7 feet thick and is underlain by a moderately weathered shale. My question is whether the moment seems to high based on a wind speed of 60 mph and if its not how do I calculate what loading it will impart to the retaining wall?