ReverenceEng
Structural
- Feb 18, 2016
- 81
Hello,
I have a client that bought a home in the middle of the build and wants to add a second story. The current engineering (not by us) has a typical raised floor, but the perimeter foundations are only 12" wide, 12" deep, and have a 6" (min.) stem wall. They are of the "L" variety.
I generally reserve the "L" foundation for slab-on-grade applications at perimeter walls (with or without curb), and I would say always use a more typical centered foundation when building a stem wall.
The PLF is still OK, but I am concerned about the eccentricity of load on the "L" foundation given that it is desired to be two stories.
Am I making mountains out of molehills, and if not, has anyone retrofitted a continuous foundation for this issue?
There is a similar thread here: but I think it is much more complicated than my situation since that thread deals with a much larger building and loads.
If need to retrofit, what are my options? It might be useful to know that the only work-in-place right now is the concrete.
1. Pour slab on grade over the strip footing similar to slab on grade?
2. Pour mat in-line with top of strip footing to brace?
3. Underpin continuous footing?
4. Pour straps between current grid of posts? This might be easiest...
Help!
I have a client that bought a home in the middle of the build and wants to add a second story. The current engineering (not by us) has a typical raised floor, but the perimeter foundations are only 12" wide, 12" deep, and have a 6" (min.) stem wall. They are of the "L" variety.
I generally reserve the "L" foundation for slab-on-grade applications at perimeter walls (with or without curb), and I would say always use a more typical centered foundation when building a stem wall.
The PLF is still OK, but I am concerned about the eccentricity of load on the "L" foundation given that it is desired to be two stories.
Am I making mountains out of molehills, and if not, has anyone retrofitted a continuous foundation for this issue?
There is a similar thread here: but I think it is much more complicated than my situation since that thread deals with a much larger building and loads.
If need to retrofit, what are my options? It might be useful to know that the only work-in-place right now is the concrete.
1. Pour slab on grade over the strip footing similar to slab on grade?
2. Pour mat in-line with top of strip footing to brace?
3. Underpin continuous footing?
4. Pour straps between current grid of posts? This might be easiest...
Help!