Hipmetal
Structural
- Dec 2, 2022
- 1
A common scenario I run into here in Indiana: Customer has a single story rectangular building with 4 CMU shearwalls (2 loadbearing, 2 non-loadbearing), steel roof bar joists, and standard 1.5" metal decking. Customer asks us to knock some big openings in one or more of the shear walls. I go do a field investigation and realize there are no drag struts connecting the roof diaphragm to any of the 4 walls (more common than not in buildings I encounter). Since I'm modifying a shear wall I feel like I am taking on responsibility for the entire horizontal force resisting system of the building. Assuming that I can justify adding the requested openings (preferably with empirical design if possible) I'll need to at least add drag struts to the 2 non-loadbearing walls. The loadbearing walls are connected to the diaphragm via embed plates welded to the bar joist, so I at least have some connection on those walls even if it relies on the joist seat not rolling over. The loadbearing walls are usually longer and have lower distributed shear loads also.
The simplest method I've come up with for retrofitting a drag strut is using a cold-formed piece of angle, maybe 16ga, installed on the underside of the deck against the CMU wall. Sheet metal screws installed from below connect the metal decking to the angle at every low rib. Self-tapping concrete anchors connect the angle to the CMU.
-Does anyone have any better solutions for this scenario?
-Is this omission in the original building construction as common everywhere else as it is here?
-Would you require the customer to install drag struts on the loadbearing walls regardless of the distributed shear loading on those walls?
Thanks
The simplest method I've come up with for retrofitting a drag strut is using a cold-formed piece of angle, maybe 16ga, installed on the underside of the deck against the CMU wall. Sheet metal screws installed from below connect the metal decking to the angle at every low rib. Self-tapping concrete anchors connect the angle to the CMU.
-Does anyone have any better solutions for this scenario?
-Is this omission in the original building construction as common everywhere else as it is here?
-Would you require the customer to install drag struts on the loadbearing walls regardless of the distributed shear loading on those walls?
Thanks