Hi All, hope you’re all well!
I am working on a customer site with lots of behind the meter generation. Power is from the supply authority with 2-off transformers, each feeding a separate main switchboard and sub boards.
The supply authority requires us to limit the total export real power in kW to a set figure. How would you accomplish this? Because the site has two separate supplies, the active power for each needs to be cal calculated and summed, and the result used in some logic to trip the breaker. Key requirement is that the trip is ‘protection grade’ and has a 400ms response time.
The options I have though of:
1) a PLC which reads the power data out of the power meters with Modbus TCP and sends a trip command via digital output. But would this be fast enough?
1) somehow providing IEC 61850 IEDs to measure the power (ie 61850 power meters) and a 61850 programmable IED ie an RTU to do the trip logic and issue a command via digital output
Thoughts?
I am working on a customer site with lots of behind the meter generation. Power is from the supply authority with 2-off transformers, each feeding a separate main switchboard and sub boards.
The supply authority requires us to limit the total export real power in kW to a set figure. How would you accomplish this? Because the site has two separate supplies, the active power for each needs to be cal calculated and summed, and the result used in some logic to trip the breaker. Key requirement is that the trip is ‘protection grade’ and has a 400ms response time.
The options I have though of:
1) a PLC which reads the power data out of the power meters with Modbus TCP and sends a trip command via digital output. But would this be fast enough?
1) somehow providing IEC 61850 IEDs to measure the power (ie 61850 power meters) and a 61850 programmable IED ie an RTU to do the trip logic and issue a command via digital output
Thoughts?