rockman7892
Electrical
- Apr 7, 2008
- 1,161
I was looking for some guidance on the pickup and time delay settings for a reverse power relay located on the main breaker of a facility which contains Co-Generation. Incoming Utility voltage is 4.16kV with M-T-M breakers set to 1200A. Generator is a 2MW gas turbine unit connected to the main 4.16kV bus though a feeder breaker. The utility has not provided any guidance and/or requirements on what to set the 32 protection at other than stating that this protection was required.
Are there particular guidelines on setting the 32 function in this application? Should it simply be set as a percentage of the generator rating or a percentage of the loading on the system? Are there specific requirements for the time delay? Does this setting need to coordinate with any other settings on the Main breakers?
Also I have seen in some cases where there is also a 67 function included in the main breaker to prevent the generator from contributing to faults on the utility system? Is this typically required in all Co-gen applications? Is there any guidance for settings this function based on the system parameters?
Thanks for the help!
Are there particular guidelines on setting the 32 function in this application? Should it simply be set as a percentage of the generator rating or a percentage of the loading on the system? Are there specific requirements for the time delay? Does this setting need to coordinate with any other settings on the Main breakers?
Also I have seen in some cases where there is also a 67 function included in the main breaker to prevent the generator from contributing to faults on the utility system? Is this typically required in all Co-gen applications? Is there any guidance for settings this function based on the system parameters?
Thanks for the help!