I have a ~50'x50' ribbed foundation for a storm water pump station. The slab will be located approximately 15 ft below grade.
The ribbed slab is 12" thick with 2 mats of reinforcing; and the beams extend an additional 16" deep, making the total section depth 28" (see below).
Our contractor has submitted an RFI requesting that they eliminate the ribs and just pour a flat mat slab that is 28" thick. As of now, they are not proposing that we alter the reinforcement setup.
If we allow the change, then I'll be in violation of minimum temperature & shrinkage steel; and probably also minimum flexural steel.
But..... ACI 318 Has the 133% exception for the flexural steel (Sect 9.6.2.1). And, ACI 350 provides provisions for only looking at the top 12" of concrete when below grade (7.12.2.1).
I'm leaning towards telling the contactor we need to add more steel if they want to do this setup; but haven't decided.
What do you think?
Thank you in advance.
The ribbed slab is 12" thick with 2 mats of reinforcing; and the beams extend an additional 16" deep, making the total section depth 28" (see below).
Our contractor has submitted an RFI requesting that they eliminate the ribs and just pour a flat mat slab that is 28" thick. As of now, they are not proposing that we alter the reinforcement setup.
If we allow the change, then I'll be in violation of minimum temperature & shrinkage steel; and probably also minimum flexural steel.
But..... ACI 318 Has the 133% exception for the flexural steel (Sect 9.6.2.1). And, ACI 350 provides provisions for only looking at the top 12" of concrete when below grade (7.12.2.1).
I'm leaning towards telling the contactor we need to add more steel if they want to do this setup; but haven't decided.
What do you think?