Baltali,
Either of those 2 details could give a full connection. Depends on Bar diameter, hook/cog bend details, wall thickness and wether or not the bar can develop full capacity at the centre of the wall.
But there are other variables. How is it being constructed? Are the walls slipformed with shear pockets, or are they poured to the underside of the slab at each floor before the slab is poured? If slipformed, I would not assume full connection
I agree with Hokie and RowingEngineer that it is conservative to assume that you cannot achieve a full connection and assume some of the negative moment capacity is lost and the moments redistribute to the bottom of the slab.
But this is a basic engineering question for you to answer. Can you develop the full bar capacity at the location where it is needed? It depends on the design code you are using and thus the bend details for the hook/cog. ACI318 development hook/cog riules for bars develop the full capacity. As3600 rules develop 50% unless you go to a lot more detail. BS8110 you need to calculate the development depending on the situation. Your design code gives you ways of determining this. You do not need to ask us.
As we do not know the answers to most of the questions I have raised, we cannot answer you. But it is simple engineering, you should not have to ask! Or if you need to ask, ask your supervisor.