Rigid Roof Insulation Weight

Status
Not open for further replies.

Boiler106

Structural
May 9, 2014
206
ASCE states that rigid roof insulation weighs 1.5 psf per inch of thickness, whereas, polyiso insulation, like Thermax, is < 0.25psf per inch.

Is there a reason why ASCE might be so much heavier? Is it assuming some sort of saturation?
 
Replies continue below

Recommended for you

ASCE tabulated weight values are known to be conservative, if you can justify a lesser weight with documentation and you need that extra weight savings then feel free to do so
 
or just a catch all for any rigid roof insulation.

Dik
 
Maybe once the membrane is shot, they assume it absorbs water :>
 
I'm looking into this at the moment and stumbled across this thread.

I have no problem using the catch-all value for normal gravity design, my issue is with the wind uplift, you would want to use a more accurate value.
 
The ASCE number is way off compared to what is typically used for rigid insulation. Use a value based on whatever product they're specifying.
 
The 1.5 psf/in is consistent with lightweight insulating concrete. Rigid board insulation is much lighter.
 