In an offshore oil filed, we need to take the barge and jack it up near the Well Head Structure (WHT) for working. Sea bed of this area is crowded with 6.6kV live cables. The intention is to safely jack the barge up for the maintenance work in the WHT. The cables shall not get damaged. All the precautions will be taken to avoid the cable damage.
Now the question is that by any chance if the cables gets damaged, what is the risk involved?
Tripping of the supply is not a problem, it is permitted.
All the cables are protected with cable differential protection (primary protection to operate in 40 to 60 msec) and the back up protection to trip in 120 msec.
Now my question is whether there is any risk for the people who are residing in the barge? or any other risk of property damage?
The barge can be earthed by connecting the same to the body of Well Head Structure (WHT) which is a permanent structure located very near and is anchored to the sea bed.
My view is that the sea water is conducting and hence the fault current will flow with in the sea water, hence there is no risk of spark over in the barge.
The barge will be connected to the WHT earth, so the barge will be at earth potential. Cable damage, in case if it happens fine for me, but the safety to persons and the other installations is important for me.
Now the question is that by any chance if the cables gets damaged, what is the risk involved?
Tripping of the supply is not a problem, it is permitted.
All the cables are protected with cable differential protection (primary protection to operate in 40 to 60 msec) and the back up protection to trip in 120 msec.
Now my question is whether there is any risk for the people who are residing in the barge? or any other risk of property damage?
The barge can be earthed by connecting the same to the body of Well Head Structure (WHT) which is a permanent structure located very near and is anchored to the sea bed.
My view is that the sea water is conducting and hence the fault current will flow with in the sea water, hence there is no risk of spark over in the barge.
The barge will be connected to the WHT earth, so the barge will be at earth potential. Cable damage, in case if it happens fine for me, but the safety to persons and the other installations is important for me.