Rolled Carpet Storage

Status
Not open for further replies.

MFS0035

Mechanical
Sep 1, 2016
1
Is anyone aware of fire sprinkler design criteria for rack storage of rolled carpet other than FMDS0830?
 
Replies continue below

Recommended for you

Travis is correct. I don't have access to GE GAP and that would be the only other source other than proprietary fire test data.
 
I had a project years ago with rack storage of rolled carpet but it was stored ~5'-10' or so. I think we used 0.6/2000 with K14 storage sprinklers.

Higher than that and there isn't anything I'm aware of.
 