I have a warehouse that I am looking at that is single story with a tilt up bearing walls around the perimeter. The building has an expansion joint running down the middle. The building is pretty repetitive and I would like to make sure I produce an economical design. The building is designed using ASCE7-05 and IBC 2009.
In accordance with ASCE7 12.10.1.1 I need to design the roof diaphragm for the same load I would design the LFRS for (Lateral Force Resisting System). When it comes to checking the diaphragm I assume I would use 0.7E to convert the strength level seismic loads to comply the allowable diaphragm loads found in the table I have from the deck mfr. Is this correct? This seems to make sense, although I have never done this before and I imagine I have been conservative.
In accordance with ASCE7 12.10.1.1 I need to design the roof diaphragm for the same load I would design the LFRS for (Lateral Force Resisting System). When it comes to checking the diaphragm I assume I would use 0.7E to convert the strength level seismic loads to comply the allowable diaphragm loads found in the table I have from the deck mfr. Is this correct? This seems to make sense, although I have never done this before and I imagine I have been conservative.