Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

Roof external welding after hydrotest

Status
Not open for further replies.

Amirrul

Petroleum
Dec 3, 2019
6
0
0
US
Dear all,

Can we perform welding repair for roof plate(fixed) after completion of hydrotest?.do we need to re hydro again after repair?. Thanks.
 
Replies continue below

Recommended for you

Yes, No. Hydro does not test the roof plate.

7.3.6 Testing of the Shell
After the entire tank and roof structure is completed, the shell (except for tanks in accordance with Annex F) shall be strength-tested and the foundation initially loaded by one of the following methods...
 

No..In case of low pressure tank as per annex F. API 650 Annex F 'F.4.4 When the entire tank is completed, it shall be filled with water to the top angle or the design liquid level, and the
design internal air pressure shall be applied to the enclosed space above the water level and held for 15 minutes. The air pressure shall then be reduced to one-half the design pressure, and all welded joints above the liquid level shall be checked for leaks by means of a soap film...'
 
Status
Not open for further replies.
Back
Top