Quick question. I have an existing building in Canada (built in 1931), upon which the owners are considering putting up a monstrous Air Handling Unit (Length = 38ft, Width = 13ft, Height = 12ft, Weight = 35,000 lbs). Now I pretty much already know without calculating anything that it won't work, but my main question was about the snow loads surrounding the unit.
If I treat it as a rooftop obstruction, I get a snow drift of 75 psf max down to 33 psf, extending for a distance of 24 ft (twice the height of the unit). If I input it as a small upper roof with a step height of 12 ft, I get 75 psf down to 33 psf, over a distance of 11 ft +/-. Would I need to consider the worst of the two conditions, or would I need to superimpose them together? Seems to me I would only need to consider the worst of the two conditions, however a 24 ft long snow drift seems kind of ridiculous??
If I treat it as a rooftop obstruction, I get a snow drift of 75 psf max down to 33 psf, extending for a distance of 24 ft (twice the height of the unit). If I input it as a small upper roof with a step height of 12 ft, I get 75 psf down to 33 psf, over a distance of 11 ft +/-. Would I need to consider the worst of the two conditions, or would I need to superimpose them together? Seems to me I would only need to consider the worst of the two conditions, however a 24 ft long snow drift seems kind of ridiculous??