It's seems this topic was touched on but not was not completely defined. Currently working on 4 story hotel, a project for Marriott using the Module 14 guidelines. Half of the guest rooms can be protected with 3 sprinklers in them and the other half have 4. Residential sprinklers have been selected using a .10 density per Mod 14. Increasing the spacing in the smaller guest room allows for one less sprinkler but at a higher pressure using (SxL) at .10.
Can the room design method be used for residential sprinklers?
Can a design area ever be less than 4 sprinklers? (using the room design method)
Provided each guest room is surrounded by a 1 hour wall, has a automatic closing door and separate calculations are provided for each of the guest rooms.
NFPA 13, 11.3.1 specifies a 4 sprinkler design area, but does not exclude the room design method.
NFPA 13, 11.2.3.3 defines the room design method but does not exclude the use of residential sprinklers or a room designed with less than 4 sprinklers.
It appears that the room design method can be used for most any hazard classification so why not residential sprinklers.
Thank for your time and this forum.
Steven Davis
It's seems this topic was touched on but not was not completely defined. Currently working on 4 story hotel, a project for Marriott using the Module 14 guidelines. Half of the guest rooms can be protected with 3 sprinklers in them and the other half have 4. Residential sprinklers have been selected using a .10 density per Mod 14. Increasing the spacing in the smaller guest room allows for one less sprinkler but at a higher pressure using (SxL) at .10.
Can the room design method be used for residential sprinklers?
Can a design area ever be less than 4 sprinklers? (using the room design method)
Provided each guest room is surrounded by a 1 hour wall, has a automatic closing door and separate calculations are provided for each of the guest rooms.
NFPA 13, 11.3.1 specifies a 4 sprinkler design area, but does not exclude the room design method.
NFPA 13, 11.2.3.3 defines the room design method but does not exclude the use of residential sprinklers or a room designed with less than 4 sprinklers.
It appears that the room design method can be used for most any hazard classification so why not residential sprinklers.
Thank for your time and this forum.