The conference room air handling unit is not holding the temperature in the space steady and worse still the supply air temp fluciates between 15 and 30 Deg C in any 30 minute spell, this causes drafts and people notice the fluciations.
I have found what I think the problem is: The air handling unit has a water heating coil at 80/70 Deg C.
The coil is only working at 10-30% of its duty most of the time. When the control valve opens say from 10 to 20% open the off coil tempetatrure takes about 15-20 minutes to settle down, it keeps rising before it stops. In the mean time if the BMS did not see a responce in the room it sends another signal to open up more so by the time the first signals responce has kicked in, the control valve is opend even further to compound the probelm.. The temp overshoots the mark in the room. When in reverse it takes ages for the heat to leave the coil and there is the same problem in reverse as the valve closes to release less heat.
Looks like the coil is just too big and a small fluciation in water flow rate takes ages for a responce. Is there stratafacation going on...ever seen probllems like this with a coil before????Any tips?
Thanks
The conference room air handling unit is not holding the temperature in the space steady and worse still the supply air temp fluciates between 15 and 30 Deg C in any 30 minute spell, this causes drafts and people notice the fluciations.
I have found what I think the problem is: The air handling unit has a water heating coil at 80/70 Deg C.
The coil is only working at 10-30% of its duty most of the time. When the control valve opens say from 10 to 20% open the off coil tempetatrure takes about 15-20 minutes to settle down, it keeps rising before it stops. In the mean time if the BMS did not see a responce in the room it sends another signal to open up more so by the time the first signals responce has kicked in, the control valve is opend even further to compound the probelm.. The temp overshoots the mark in the room. When in reverse it takes ages for the heat to leave the coil and there is the same problem in reverse as the valve closes to release less heat.
Looks like the coil is just too big and a small fluciation in water flow rate takes ages for a responce. Is there stratafacation going on...ever seen probllems like this with a coil before????Any tips?
Thanks