Hi have a major problem with a conference room that has its own dedicated air handling unit with heating and cooling coil
The room is only about 15m x 10m. It has 6 no. side wall supply air linear grilles (built into a bulkhead all around the room) with the blade tips facing down deflecting the air into the room and downwards towards the occupanct. The room sensor is on the wall under the bulkhead so there is no direct air flow onto the sensor.
The problem is im constatnly getting calls that it is too hot, too cold....too hot, really hot, reallly cold...I am been driven mad. The designers have cleared off!
From the BMS I can see that the room sensor is holding the room ( ie. the area around the sensor at 21-23 deg C which is OK but if i look at the supply air temp from the air handling unit it varies between 14 and 30 deg C in the matter of less than an hour.
I have a feeling that it is the draft caused by the side wall linear grille onto people that is causing the discomfort, especially if it varies from 14 -30 in the space of half an hour.
Should I change the grilles to ceiling mounted diffusers. I can do this easy, i have a T bar ceiling wiht lay in ceiling tiles. I feel this is my only option and would eliminate drafts. The air will not hit people directly and the swirl type have never caused problems for me. The BMS guys says he has tried every thing from slowing down to speeding up the loops and only looks at the room sensor and says its holding
Please help, my job depends on it at this stage the MD is going to get me if i dont sort it.! Its been going on 6 months since I built it.
Thanks!
The room is only about 15m x 10m. It has 6 no. side wall supply air linear grilles (built into a bulkhead all around the room) with the blade tips facing down deflecting the air into the room and downwards towards the occupanct. The room sensor is on the wall under the bulkhead so there is no direct air flow onto the sensor.
The problem is im constatnly getting calls that it is too hot, too cold....too hot, really hot, reallly cold...I am been driven mad. The designers have cleared off!
From the BMS I can see that the room sensor is holding the room ( ie. the area around the sensor at 21-23 deg C which is OK but if i look at the supply air temp from the air handling unit it varies between 14 and 30 deg C in the matter of less than an hour.
I have a feeling that it is the draft caused by the side wall linear grille onto people that is causing the discomfort, especially if it varies from 14 -30 in the space of half an hour.
Should I change the grilles to ceiling mounted diffusers. I can do this easy, i have a T bar ceiling wiht lay in ceiling tiles. I feel this is my only option and would eliminate drafts. The air will not hit people directly and the swirl type have never caused problems for me. The BMS guys says he has tried every thing from slowing down to speeding up the loops and only looks at the room sensor and says its holding
Please help, my job depends on it at this stage the MD is going to get me if i dont sort it.! Its been going on 6 months since I built it.
Thanks!