I've been working in the I&C Field for years in Petrochemical, Refining, Power, and Water/WasteWater. I'm no salesperson....but, maybe its time for a switch...I could use the raise...
Like I said above, I've never seen a ground wire landed on the internal or external ground screw.
Just to clear up any confusion, lets keep in mind I'm not talking about the *Shield* wire thats normally cut back, wrapped around the single conductors, and taped off in the transmitter housing. I'm actually talking about a ground conductor, not the shield provided in a twisted shielded pair.
I found the info right in the manual provided by Rosemount.
Page 2-43
"NOTE
The transient protection terminal block does not provide transient protection
unless the electronics case is properly grounded. Do not run the transient
protection ground wire with field wiring because the transient protector ground
wire may carry excessive current if a lightening strike occurs. Grounding the
electronics case using a threaded conduit connection may not provide
sufficient ground."
Thats out of the manual for the 3095. during a search I believe I found it in the 3051 manual as well.