Hi,
I'm sitting with this paper machine drive. AC drives. Unruly speed, nothing wrong with drive. Mechies say nothing wrong with machine.
Had a look at motor current. Heavy side-bands (about 15 percent of fundamental). Checked other motors with same load. Side-bands below 1 percent.
Question: Shall I tell them to stop the machine and change motor? Do you think that 15 percent side-bands is a strong enough indication for rotor problems. I will hang if I stop the machine, change motor (250 kW) and it doesn't help. HELP!!
Gunnar Englund