Is there a limitation on the spacing of the vertical reinforcing around the perimeter of a round concrete column. With round ties, is it to be limited to 6" per ACI 318? Or do round ties let me go further than 6"?
 
Replies continue below

Recommended for you

I think you can go further than 6", but you have to have at least 8 bars (ACI 10.9.2)and you have to meet the 1% minimum. In 7.10.5.3 - the last sentence appears to imply that if you use circular ties, the 6" space limit doesn't apply.

 
Actually ACI 10.9.2 requires only 4 bars minimum for square or circular ties, and 6 bars minimum for spirals.

Aside from meeting the 1% min and 8% max steel area I don't think the vertical bar spacing matters for circular ties.
 
I think what JAE was implying is when 8 bars or more are provided you do not have to consider the bar placement when considering its moment strength.
 