Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Tek-Tips community for having the most helpful posts in the forums last week. Way to Go!

RS-232

Status
Not open for further replies.

fapsa

Industrial
May 31, 2003
11
0
0
US
I have a Programmable operator interface that gets damage because of the environment that it's in and needs to be moved away from the PLC 150ft, it uses RS-232, but the manufacture says that with RS-232 can go up to only 50ft without having problems, is there something to convert from RS-232 to another protocol that can go the 150ft then go back to RS-232?
Thanks
 
Replies continue below

Recommended for you

At what speed? RS-232 can go WAY farther than 50', depending upon baudrate... I'm running a bi-directional link for 200'+ at 9,600.

Dan - Owner
Footwell%20Animation%20Tiny.gif
 
Status
Not open for further replies.
Back
Top